Hello! Log in or Register   |  Help  |  Donate  |  Buy Shirts See all banner ads | Advertise on TheSamba.com  
TheSamba.com
 
DIY - Red Tek conversion
Page: Previous  1, 2, 3 ... 56, 57, 58, 59, 60  Next
Jump to:
Forum Index -> Vanagon Share: Facebook Twitter
Reply to topic
Print View
Quick sort: Show newest posts on top | Show oldest posts on top View previous topic :: View next topic  
This page may contain links to eBay where the site receives compensation.
Author Message
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sat Jul 21, 2018 7:12 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Both Dave(s) are spot on. You can also use a very fine water mist in lieu of fans at the condenser. The condenser doesn't care what fluid you use. The advantage of using water is that you can set (within reason) the head pressure you want to work with. Try the water mist, don't get crazy, just a mist, try to set your head pressure at 190 psig or so.

With your system running you should be able to slowly bleed off refrigerant from the low side with very little oil loss. I doubt you've lost enough oil to be concerned about it at this time. Monitor vent temps while doing this.

Your suction pressure seems a bit low considering your current head pressure and ambient temps. May need to look into that when/if you get comfortable with the charge.

Is the sight glass on your gauges in the center of the manifold? If so, the only time it should "see" refrigerant is when you are charging the system. If it's coming from the high side something is not right.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
fxr
Samba Member


Joined: December 07, 2014
Posts: 2321
Location: Bay area CA
fxr is offline 

PostPosted: Sat Jul 21, 2018 7:16 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Farf wrote:
If it's coming from the high side something is not right.

If it's coming from the high side then the high pressure valve on the manifold set is open - hopefully just a faulty valve (HF will replace without question) - or perhaps a beginner's mistake (we've all made them).
_________________
Jim Crowther
1984 1.9l EJ22 Westy Wolfsburg Edition
Vespa GTS 300
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sat Jul 21, 2018 7:29 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

By the way, what was your total oil charge when you buttoned the system up?
One of the symptoms of an oil overcharge is quoted below.

"Evaporator temperatures and pressures may run low because of the reduced heat transfer from the oil insulating the evaporator tubes."

https://www.achrnews.com/articles/88145-oil-logged-evaporators

If there is lots of oil your head pressures may run higher too.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
dhaavers
Samba Member


Joined: March 19, 2010
Posts: 7756
Location: NE MN (tinyurl.com/dhaaverslocation)
dhaavers is offline 

PostPosted: Sat Jul 21, 2018 7:49 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Farf wrote:
You can also use a very fine water mist in lieu of fans at the condenser...

This reminds me that I also did this with good results. Thanks, Farf! Cool

- Dave
_________________
86 White Wolfsburg Westy Weekender
"The WonderVan"

<EDITED TO PROTECT INNOCENT PIXELS>
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sat Jul 21, 2018 8:00 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Another thing to check from the linked article from my previous post:

"Low compressor superheat: If the TXV is running low superheat, this will cause the compressor superheat to run lower."

While you are running the system grab hold of the suction line at the compressor is it cold or warm?
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sat Jul 21, 2018 9:38 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Generic Pressure/Enthalpy chart showing the refrigeration cycle.
Image may have been reduced in size. Click image to view fullscreen.

A bit "techie" but important to understand. Refrigerant flow is CCW.

Basic info that is contained on the HC-12A chart:
Image may have been reduced in size. Click image to view fullscreen.


HC-12A Pressure/Enthalpy chart with Utahn's high and low pressure (generally) plotted. Unknowns are superheat/subcooling.
Image may have been reduced in size. Click image to view fullscreen.


HyChill's PH chart matches RedTek perfectly. The area under the curve represents what you see on Redtek's Pressure/Temperature chart. If you know what your superheat and subcooling values are troubleshooting becomes quite simple. In a nut shell a properly plotted PH chart tells you where the refrigerant is and what it's doing (or should be doing) at any point in the system. kind of a sneak peak inside.

This is just information for general consumption. It's pretty rare to have to plot one of these, but I think it's a good visual aid in understanding the refrigeration cycle in terms of pressure and temperature. A lot more info on this via the internet for those who may be interested enough to look further into it.

When I get off my fat A$$ and get around to fixing my A/C I'll plot my system out for you.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Westaru
Samba Member


Joined: October 10, 2016
Posts: 189
Location: Utah
Westaru is offline 

PostPosted: Sun Jul 22, 2018 11:04 am    Post subject: Re: DIY - Red Tek conversion Reply with quote

Quote:
High pressure high side is a result of the gas being unable to drop the heat at the condensor.

You need some serious cooling air flow through the radiator.


I had 2 box fans at the front, but the garage was pretty hot (almost 100*). I'll need to figure out something different next time.



Quote:
FWIW, I had similarly poor vent temps until I tried charging with the engine
cover laid in place (to keep engine heat out of the cabin) & hatch closed as
much as possible (to recirculate cooled air inside cabin). YMMV...


This is a great idea! Does it make a difference in the charging process, or only with vent temps?

Quote:
Both Dave(s) are spot on. You can also use a very fine water mist in lieu of fans at the condenser. The condenser doesn't care what fluid you use. The advantage of using water is that you can set (within reason) the head pressure you want to work with. Try the water mist, don't get crazy, just a mist, try to set your head pressure at 190 psig or so.

With your system running you should be able to slowly bleed off refrigerant from the low side with very little oil loss. I doubt you've lost enough oil to be concerned about it at this time. Monitor vent temps while doing this.

Your suction pressure seems a bit low considering your current head pressure and ambient temps. May need to look into that when/if you get comfortable with the charge.

Is the sight glass on your gauges in the center of the manifold? If so, the only time it should "see" refrigerant is when you are charging the system. If it's coming from the high side something is not right.


The water mist is a great idea! I will try this next time as well as removing the upper and lower grill to faciliate additional air flow.

To clarify - I would bleed from the low side with the system running?

Head pressure comes down quickly when the high side fan comes on... What causes low suction pressure and high head pressure?

My sight glass is in the center of the manifold. High pressure gauge open and monitoring high side, charging through low side with the Redtek gauge monitoring low side.

Quote:
If it's coming from the high side then the high pressure valve on the manifold set is open - hopefully just a faulty valve (HF will replace without question) - or perhaps a beginner's mistake (we've all made them).


High side pressure valve was open while charging to monitor those pressures. Was this incorrect? I was under the impression I should monitor both high and low side while charging.

Quote:
By the way, what was your total oil charge when you buttoned the system up?
One of the symptoms of an oil overcharge is quoted below.

"Evaporator temperatures and pressures may run low because of the reduced heat transfer from the oil insulating the evaporator tubes."

https://www.achrnews.com/articles/88145-oil-logged-evaporators

If there is lots of oil your head pressures may run higher too.


Great idea... I filled the system with 6.2oz of oil per the Haynes manual and spec on the Subaru Calsonic compressor, compressor was drained (new compressor) prior to doing this. That syncs up pretty well with how much the original system had, but Smallcar says the whole system should only get 2oz with a new compressor and 3oz with a used. That seemed awfully low and not correct.

Quote:
Another thing to check from the linked article from my previous post:

"Low compressor superheat: If the TXV is running low superheat, this will cause the compressor superheat to run lower."

While you are running the system grab hold of the suction line at the compressor is it cold or warm?


Suction line was cold if I recall correctly. I'll try it again today and check it again. Thank you for the diagrams and information - I'm going to need to read those a few times to begin understanding them!
_________________
1984 'Westaru' Vanagon Westfalia EJ22
@UtahWestfalia on IG
Back to top
View user's profile Send private message Instagram Gallery Classifieds Feedback
dlb154
Samba Member


Joined: December 27, 2006
Posts: 359
Location: Reno, NV
dlb154 is offline 

PostPosted: Sun Jul 22, 2018 11:13 am    Post subject: Re: DIY - Red Tek conversion Reply with quote

Anyone use "Kwik Charge" to speed up low side charge?



https://www.amazon.com/Imperial-535-C-Charge-Liqui...FZ7321A1HP

Product claims you invert the can and the device "flashes" the liquid to vapor so you don't damage the compressor.

Image may have been reduced in size. Click image to view fullscreen.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sun Jul 22, 2018 12:22 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Your high side gauge does not need to be open to monitor high side pressure and definitely should not be open when charging the system. The pressures you had listed are now suspect. Measure the pressures again with both manifold valves shut. It's good that your head pressure responds well to additional airflow.

Yes, slowly bleed off refrigerant from the low side while the system is running. Don't forget to monitor vent temps. If you get lots of oil coming out with it I would question the amount of oil you have in the system. Based on what Small Car says about the amount of oil needed vs. what you put in needs to be figured out, something not lining up there.

The cold suction line may suggest that you are overfeeding the evaporator. Too much oil in the system as stated earlier is one cause of this. Another cause could be that RedTek is a blend with a 14F temperature glide and your TXV is set for 134A so you may have issues with the superheat adjustment.

Seems like at this point you should concentrate your efforts on finding out what the correct oil charge should be.

Is it possible for you to measure the liquid line temp after the R/D and the suction line temp at the compressor. If so, do not use an IR thermometer. This would tell us a lot about what's going on in the system.

Closing up the engine compartment and the van itself will help with your efforts.

A brief write up on superheat/subcooling and why it's important.

https://www.contractingbusiness.com/service/subcooling-and-superheat-superheroes-system-charging
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sun Jul 22, 2018 1:20 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Should add that if you feel the need to check line temps something like this would work well. You can spend a bit more money and get a thermometer with a pipe clamp type sensor. But I think this one or similar is all you would need.

https://www.amazon.com/Dodolight-Digital-Channel-Thermometer-Thermocouple/dp/B0084JQL1Q

And I should point out that you need to sample the temps on the metal piping in the system and not on the barrier hose itself. You should also insulate the sensor and pipe to ensure accurate measurements.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
RufusRockwell
Samba Member


Joined: July 20, 2010
Posts: 116
Location: Oregon
RufusRockwell is offline 

PostPosted: Sun Jul 22, 2018 5:30 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Quick detour...
I've been running Red Tek in my 85 tin top and it is a wonderful improvement over the r134. However, I'm getting ready to swap in an EJ22 and will need to evacuate the AC system. What are my options? I've contacted Red Tek but haven't heard back and the local shop won't do it. Can it be safely vented into the atmosphere (far from a flame)???
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sun Jul 22, 2018 6:47 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Vent away...

https://www.epa.gov/snap/final-rule-protection-str...on-and-air

Open the fact sheet PDF you're good to go.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
RufusRockwell
Samba Member


Joined: July 20, 2010
Posts: 116
Location: Oregon
RufusRockwell is offline 

PostPosted: Sun Jul 22, 2018 10:06 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Thanks!
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Westaru
Samba Member


Joined: October 10, 2016
Posts: 189
Location: Utah
Westaru is offline 

PostPosted: Mon Jul 23, 2018 11:15 am    Post subject: Re: DIY - Red Tek conversion Reply with quote

Farf wrote:
Your high side gauge does not need to be open to monitor high side pressure and definitely should not be open when charging the system. The pressures you had listed are now suspect. Measure the pressures again with both manifold valves shut. It's good that your head pressure responds well to additional airflow.

Yes, slowly bleed off refrigerant from the low side while the system is running. Don't forget to monitor vent temps. If you get lots of oil coming out with it I would question the amount of oil you have in the system. Based on what Small Car says about the amount of oil needed vs. what you put in needs to be figured out, something not lining up there.

The cold suction line may suggest that you are overfeeding the evaporator. Too much oil in the system as stated earlier is one cause of this. Another cause could be that RedTek is a blend with a 14F temperature glide and your TXV is set for 134A so you may have issues with the superheat adjustment.

Seems like at this point you should concentrate your efforts on finding out what the correct oil charge should be.

Is it possible for you to measure the liquid line temp after the R/D and the suction line temp at the compressor. If so, do not use an IR thermometer. This would tell us a lot about what's going on in the system.

Closing up the engine compartment and the van itself will help with your efforts.

A brief write up on superheat/subcooling and why it's important.

https://www.contractingbusiness.com/service/subcooling-and-superheat-superheroes-system-charging


Thank you again Farf! It looks like I was using the gauges incorrectly and had the manifold high side open the whole time (thought I needed it open to measure pressures). Messed this one up pretty good and considering bleeding off all the refrigerant and starting over from vacuum. With the high side line full of refrigerant I don't have any way of knowing how much I have in the system.

I can't explain the amount of oil Smallcar recommends - it doesn't make any sense. I should be around 6.2oz based upon what the stock system holds + what my new calsonic compressor calls for (I added up the stock system, subtracted the stock compressor and added the Calsonic). I have a 16x24" condenser which is larger than stock as well. But SC swears 2 oz is all that is needed - why would that be? Just the lines, condenser and compressor should account for more than this. Or am I missing something?

Here is what I've found in my research:

- Calsonic Compressor per Subaru shop manual: 3.2oz
- Evaporator 2.02 oz (Bentley 87.7 from 1986)
- Accumulator 0.3 oz (Bentley)
- High Pressure Hose 0.3 oz (Bentley)
- Low Pressure Hose 0.3 oz (Bentley)
- Total Oil = 5.92 oz...
- Condenser is never mentioned in the Bentley so I didn't factor it in even though my condenser is larger than stock (16x24 parallel flow)


I can measure the line temps easily using an IR camera (FLIR) or a thermopen - believe the first would be more accurate? I will add that even with R134A my suction line was cold at the compressor (total system had 2.06# of R134A).

Do any of you feel like there is a good performance gain (i.e. cooling) of Redtek/Envirosafe vs R134A, or is the benefit just lower pressures and better compatibility with an R12 system?
_________________
1984 'Westaru' Vanagon Westfalia EJ22
@UtahWestfalia on IG
Back to top
View user's profile Send private message Instagram Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Mon Jul 23, 2018 1:47 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Other than the Small Car evaporator being smaller and a marginal bit of hose layout i think your oil charge is probably ok.

Measure the lines with both thermometers and see what you come up with. I'm not sure that the IR gun will give you an accurate enough temperature.

Advantages of using RedTek over 134A. My personal opinion is both are fine to use with the nod going to RedTek. I think the 134A could use an even larger condenser than the upgraded ones people have been installing here. The disadvantage as I see it, is that some have had problems with their TXV's using RedTek.

I have to replace my TXV and have ordered one that the superheat can be adjusted externally without having to open the system. No big hurry on my part as I usually camp/drive above 8000'.

Looking at he chart from RedTek (last line), you can see that the 12A has a much higher latent heat capacity than 134a and R12. To get the same refrigeration capacity as R12 the mass of refrigerant (12A) required, reduces. the same holds true with 134A.

Image may have been reduced in size. Click image to view fullscreen.
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Tue Jul 24, 2018 11:48 am    Post subject: Re: DIY - Red Tek conversion Reply with quote

For those of you interested, here's the Sanden (compressor) guide to using super-heat/sub-cooling for charging and troubleshooting. If you are using the RedTek pressure/temperature chart you need to use the bubble point column for super-heat and the dew point column for sub-cooling.

All of the info gathered on the worksheet can them be plotted (if you feel the need) on the PH chart for a visual representation of your system.

Note: I have a minor disagreement on Sanden's subcooling method due to the existence of the Receiver/Drier. This just changes the location of where I would sample temps for sub-cooling.

Once you understand this method, you probably know more about how the system works than most automotive a/c techs.

www.sanden.com/objects/3%20-%20Troubleshooting%20%20-%20Web_01.pdf
Back to top
View user's profile Send private message Gallery Classifieds Feedback
Inlet
Samba Member


Joined: April 12, 2010
Posts: 287
Location: SF Bay Area
Inlet is offline 

PostPosted: Fri Jul 27, 2018 8:44 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

I purchased the Sanden 805 / 6630 compressor, without realizing the connections are #8 and #10, my 84 westy has two equal size threaded connections that are bigger than the #10. I'm soo close to getting this system going again, but now feel like I took two steps back. Are there adapters for this?
Back to top
View user's profile Send private message Gallery Classifieds Feedback
kourt
Samba Member


Joined: August 13, 2013
Posts: 1941
Location: Austin, TX
kourt is offline 

PostPosted: Sat Jul 28, 2018 9:26 am    Post subject: Re: DIY - Red Tek conversion Reply with quote

Just a note--my SmallCar system runs better on R134 than RedTek, and I am sure it is due to the TXV provided with the SmallCar system, which is designed for R134. I may have to look into the adjustable TXV in the future--I liked the convenience and pricing of RedTek.

kourt
Back to top
View user's profile Send private message Send e-mail Gallery Classifieds Feedback
Farf
Samba Member


Joined: July 12, 2009
Posts: 463
Location: Colorado
Farf is offline 

PostPosted: Sat Jul 28, 2018 1:11 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Kourt or anyone interested,

Here's a decent looking TXV that is sized perfectly for the Small Car A/C. Medium temp application and internally equalized. You would need adapters to go from O-ring to flare or if you are still building yours I believe you can go straight from barrier hose to female flare with fittings. Can be used for 134A or RedTek, would need superheat adjusted.

Note: I don't know if it will fit in the area that Small Car allocated for the existing TXV. Edit: I should add that you need access to the valve while the system is running. May not be possible on the SC system.

https://www.ebay.com/itm/Parker-C2FW-3-8X1-2-SAE-T...;rt=nc[/b]
Back to top
View user's profile Send private message Gallery Classifieds Feedback
kourt
Samba Member


Joined: August 13, 2013
Posts: 1941
Location: Austin, TX
kourt is offline 

PostPosted: Sat Jul 28, 2018 5:40 pm    Post subject: Re: DIY - Red Tek conversion Reply with quote

Thanks for that link. I tried RedTek for two years in both my 91 Vanagon and my 87 Volvo 240. Both have all new lines, parallel flow condensers, new evaporators, and new compressors--but the expansion valves were both built for R134. My wife went out of her way to thank me when I switched back to R134 in the Volvo, as it was such an improvement from RedTek.

Part of the problem is we have super hot summers in central Texas. Only so much heat rejection can occur on a 108 degree day like yesterday.

kourt
Back to top
View user's profile Send private message Send e-mail Gallery Classifieds Feedback
Display posts from previous:   
Reply to topic    Forum Index -> Vanagon All times are Mountain Standard Time/Pacific Daylight Savings Time
Page: Previous  1, 2, 3 ... 56, 57, 58, 59, 60  Next
Jump to:
Page 57 of 60

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum

About | Help! | Advertise | Donate | Premium Membership | Privacy/Terms of Use | Contact Us | Site Map
Copyright © 1996-2023, Everett Barnes. All Rights Reserved.
Not affiliated with or sponsored by Volkswagen of America | Forum powered by phpBB
Links to eBay or other vendor sites may be affiliate links where the site receives compensation.