69diamondblueT1 Samba Member
Joined: January 11, 2015 Posts: 9 Location: Whidbey Island, Washington
|
Posted: Sun Apr 18, 2021 5:38 am Post subject: Shurflo faucet troubleshooting |
|
|
Good morning all! I have a 1987 Westy (Canadian) and just installed the Shurflo faucet upgrade from GoWesty. As soon as I connect the wires to the OG VW harness leads that go to the pump, the pump turns on no matter what the position of the faucet switch. I tried reversing the wire connections, same issue. I hooked a multi-meter up to the faucet and no matter what position I rotate the switch on the faucet, the meter reads 0 ohms resistance; continuity never is broken by the switch. I'm guessing that I may have just received a faulty faucet but want to make sure that I didn't miss anything. My Westy has a below cabinet pump (not submerged). I appreciate any help that you can provide. Thanks! _________________ 1962 Beetle "Bucky" bone stock
1987 Westy "Dharma"
Past projects
1955 Beetle "Bridgette" RIP!!
1969 Beetle “Genevieve” resto-mod California
1974 Tin top camper “Molly” stock resto |
|
Back to top |
|
 |
MarkWard Samba Member

Joined: February 09, 2005 Posts: 18751 Location: Retired South Florida
|
Posted: Sun Apr 18, 2021 6:41 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
It does sound defective. As a test, you could disconnect the faucet wires and see if you can operate the pump touching the 2 wires together. I’ve never really paid attention to the valve enough to notice if there was a click at the off point. |
|
Back to top |
|
 |
kamzcab86 Samba Moderator

Joined: July 26, 2008 Posts: 8453 Location: Arizona
|
Posted: Sun Apr 18, 2021 8:49 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
MarkWard wrote: |
I’ve never really paid attention to the valve enough to notice if there was a click at the off point. |
The Shurflo clicks on/off, so ensure that the faucet knob is, in fact, being rotated to the fully off position. _________________ ~Kamz
1986 Cabriolet: www.Cabby-Info.com
1990 Vanagon Westfalia: Old Blue's Blog
2016 Golf GTI S
"Real knowledge is to know the extent of one's ignorance." - 孔子 |
|
Back to top |
|
 |
jimf909 Samba Member

Joined: April 03, 2014 Posts: 8168 Location: WA/ID
|
Posted: Sun Apr 18, 2021 11:04 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
^^^ True. I clearly hear an audible snap or click when turning the knob to switch the pump (I just double checked). The click is the contact snapping from open to close or vice versus.
Here's a thread on dissecting it but if twisting the knob doesn't do it, it sounds defective.
https://www.thesamba.com/vw/forum/viewtopic.php?t=704908
|
|
Back to top |
|
 |
69diamondblueT1 Samba Member
Joined: January 11, 2015 Posts: 9 Location: Whidbey Island, Washington
|
Posted: Mon Apr 19, 2021 5:31 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
thanks for the tips all. I tested connecting the two wires from the pump together with a quick jumper and, yes, it engages the pump. I also can hear the audible click in the shur-flo, but there's still continuity no matter which position the dial is in, fully off, fully on, throughout the whole rotation. I tested the Delta-six and it breaks continuity as it is supposed to when its in the off position. Never had a problem with the delta-six other than the tip of the fitting that the water hose attaches to being cracked which is why I am replacing it.
Amazon sells the same faucet and under its 2 star reviews, someone had the same issue; switch clicked, but pump was constantly on. They disassembled the faucet and found that the wires had been soldered together during production. I emailed GoWesty tech support and am hoping that they send me another one. They have awesome customer support and always seem to resolve any questions that I've had with their products. _________________ 1962 Beetle "Bucky" bone stock
1987 Westy "Dharma"
Past projects
1955 Beetle "Bridgette" RIP!!
1969 Beetle “Genevieve” resto-mod California
1974 Tin top camper “Molly” stock resto |
|
Back to top |
|
 |
danielheff Samba Member

Joined: January 22, 2016 Posts: 174 Location: San Diego, CA
|
Posted: Sat Oct 05, 2024 7:34 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
After a few months of my faucet having intermittent issues (would only engage the pump after vigorous jiggling) it finally stopped all together. I temporarily rigged the yellow wires for the pump to a switch to still be able to use the tank but this was not the ideal setup. I think this has been mentioned before, but adding a relay to deliver power to the pump solved the problem immediately. I didn’t replace the pump, just grounded one wire from the pump and ran the other wire to the relay. I like switching a ground wire through the faucet rather than having 12v+ always live in the switch handle. I still need to clean up wiring, but there’s all kinds of room for gadgets under the sink and behind the top drawer.
_________________ '70 Squareback 1835cc
'85 Vanagon GL Camper, EJ22, Peloquin Diff, Burley rear disc brakes, SC big front brakes, Espar D2L, 250ah Lifepo4
'85.5 944 NA |
|
Back to top |
|
 |
harvgwen Samba Member
Joined: February 11, 2021 Posts: 292 Location: Okanagan Valley, British Columbia
|
Posted: Sat Oct 05, 2024 8:36 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
I did the same on mine, at the advice of someone else on this forum. It’s also worked great ever since. _________________ 1986 Westfalia Vanagon, 2.2 Subaru
Okanagan Valley, British Columbia |
|
Back to top |
|
 |
Bill D Samba Member
Joined: December 06, 2011 Posts: 104
|
Posted: Fri Oct 25, 2024 9:43 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
I'm having the same problem with my Shurflo faucet... would appreciate if you could give me specific directions on how to perform the 'relay trick'... Like what relay and which terminals on the relay get hooked to which wires???
Thanks
Bill |
|
Back to top |
|
 |
harvgwen Samba Member
Joined: February 11, 2021 Posts: 292 Location: Okanagan Valley, British Columbia
|
Posted: Sat Oct 26, 2024 1:31 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
You want to connect your main power wire for your pump to pin 30 of the relay. (4 pin relay is good). Then connect a same (or heavier) wire to pin 87 of the relay, and connect it to the pump. This is your pump power. The pump ground will be unchanged. There are 2 ways you could connect your faucet across the other 2 pins of the relay. I’ll suggest you piggyback a faucet wire to your pin 30 connection. This wire goes to your faucet (switch). The other wire coming from your faucet will get connected to relay pin 86. Then to complete your circuit, connect a wire to relay pin 85 and connect the other end of that wire to ground. This way the main power for the pump doesn’t pass through the faucet switch. I suspect that my explanation isn’t terribly good. I’m not a teacher.
https://m.youtube.com/watch?v=HmiqUZ0sRt4
Or google “how to connect a 4 pin relay” _________________ 1986 Westfalia Vanagon, 2.2 Subaru
Okanagan Valley, British Columbia |
|
Back to top |
|
 |
Bill D Samba Member
Joined: December 06, 2011 Posts: 104
|
Posted: Sat Oct 26, 2024 2:15 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
Thanks for the relay tutorial HarvGwen... I have much experience with relays... wondering if those terminal numbers you gave are the same for all relays??? Or are those unique to the VW/Vanagon world relays? Any particular brand of relay?
thanks,
Bill |
|
Back to top |
|
 |
Bill D Samba Member
Joined: December 06, 2011 Posts: 104
|
Posted: Sat Oct 26, 2024 2:16 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
Er... also... when you say after the relay solution you Shurflow has worked ever since, how long would that be? Months, years?
thanks again,
Bill |
|
Back to top |
|
 |
harvgwen Samba Member
Joined: February 11, 2021 Posts: 292 Location: Okanagan Valley, British Columbia
|
Posted: Sat Oct 26, 2024 2:28 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
Relay numbers are standard. _________________ 1986 Westfalia Vanagon, 2.2 Subaru
Okanagan Valley, British Columbia |
|
Back to top |
|
 |
harvgwen Samba Member
Joined: February 11, 2021 Posts: 292 Location: Okanagan Valley, British Columbia
|
Posted: Sat Oct 26, 2024 2:29 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
At least a year. It might be two years. _________________ 1986 Westfalia Vanagon, 2.2 Subaru
Okanagan Valley, British Columbia |
|
Back to top |
|
 |
Bill D Samba Member
Joined: December 06, 2011 Posts: 104
|
Posted: Sun Oct 27, 2024 3:17 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
Ok.. HarvGwen... out in the garage with faucet and relay and trying to follow your directions...
Questions:
1) "connect your main power wire for your pump to pin 30" So, that's one of the two yellow wires that the original faucet connected to, right? The one what meters 12v right?
2) "Then connect a same (or heavier) wire to pin 87..." So, that's the other yellow wire?
3) Faucet wires... So, one goes to pin 30 and the other to pin 86, right?
But... if the purpose of doing this relay to not be passing the full amperage draw of the pump thru the faucet switch, is this right to be connecting the faucet wire to pin 30 where the main power wire for the pump is also located???
I'm a bit confused...
Thanks,
Bill |
|
Back to top |
|
 |
dabaron Samba Member

Joined: June 21, 2018 Posts: 2716 Location: Philly, mang
|
Posted: Sun Oct 27, 2024 3:32 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
just added a relay and mine is working great
_________________ 1991 Vanagon GL Camper
i had no idea i wanted to be a mechanic |
|
Back to top |
|
 |
Bill D Samba Member
Joined: December 06, 2011 Posts: 104
|
Posted: Mon Oct 28, 2024 8:27 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
Thanks for the wiring schematic... that helps a lot !
Also watched a YouTube video explaining relays... helpful also.
One thing I don't understand is why the 85-86 pathway does not draw the same amount of amps as the 30 - 87 path? Guess that maybe it's just the resistance of the very small coil wire? or is there and actual resistor built into relays?
thanks,
Bill |
|
Back to top |
|
 |
crazyvwvanman Samba Member

Joined: January 28, 2008 Posts: 10372 Location: Orbiting San Diego
|
Posted: Mon Oct 28, 2024 9:29 am Post subject: Re: Shurflo faucet troubleshooting |
|
|
The main reason is the total length of the very thin coil wire inside the relay is very long.
The resistance of the coil wire is small but when you multiply it by the total length it becomes much larger and this limits the current flow.
If you find the specs of a relay one of the specs is the total resistance of the long coil winding.
Mark
Bill D wrote: |
Thanks for the wiring schematic... that helps a lot !
Also watched a YouTube video explaining relays... helpful also.
One thing I don't understand is why the 85-86 pathway does not draw the same amount of amps as the 30 - 87 path? Guess that maybe it's just the resistance of the very small coil wire? or is there and actual resistor built into relays?
thanks,
Bill |
|
|
Back to top |
|
 |
Timwhy Samba Member

Joined: January 01, 2009 Posts: 4091 Location: Maine
|
|
Back to top |
|
 |
MsTaboo  Samba Member

Joined: June 02, 2006 Posts: 4549 Location: East Kootenay, British Columbia
|
Posted: Mon Oct 28, 2024 2:52 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
I don't think that would fit under the Westy sink top. Will it clear the sides enough to allow the top to close?
Reviews say it's pretty flimsy and prone to breaking. _________________ Currently:
'90 Syncro Westy 3 knob w/Zetec
The information age has morphed into the age of disinformation and willful ignorance. Agnotology!
All that's needed for evil to prevail is for good people to do nothing.
Resist Kleptocratic Oligarchy (and Idiocracy)! |
|
Back to top |
|
 |
harvgwen Samba Member
Joined: February 11, 2021 Posts: 292 Location: Okanagan Valley, British Columbia
|
Posted: Mon Oct 28, 2024 8:30 pm Post subject: Re: Shurflo faucet troubleshooting |
|
|
Bill, the reason for the high current draw through 30 to 87 is because it powers the pump. Whatever current the pump draws flows through the relay from 30 to 87. The high current no longer runs through your Shur Flo switch. The low current draw in the 85 to 86 part of the relay is the small amount of current needed to pull the relay switch to the closed position. That small current is what now flows through your Shur Flo switch. The Shur Flo switch isn’t robust enough for the high current that the pump needs. The relay now becomes the switch for the pump. The relay is made to take the higher current.
The wiring diagram provided above is very similar to what I suggested, except that I had the Shur Flo switch on the positive side of the relay. The diagram has it on the negative side. It will work the same. _________________ 1986 Westfalia Vanagon, 2.2 Subaru
Okanagan Valley, British Columbia |
|